Afternoon,
We currently have a gas range cook top with electric oven underneath that is hooked up to a 40 amp breaker via 8/3 romex wire. We are replacing this with an all gas range/oven that only requires 120 volts/15 amp breaker. My question is can I use the existing 8/3 wire by splicing 12/2 via one junction box at the service panel end and another box in an accessible spot just before the new oven, capping off the red wire at both ends? I'd then replace the 40 amp breaker with a 15 amp and connect 12/2, then connect the other spliced 12/2 into a new receptacle for the oven.
My original plan was just to attach fishing wire to the existing 8/3, pull out the 8/3 from the service panel, then attach 12/2 to the fishing wire and fish that through to the service panel. I will go this route if I have to but it involves several cuts into drywall, undoing bulkheads and acoustic tiles, etc.
electrical oven
add a comment |
Afternoon,
We currently have a gas range cook top with electric oven underneath that is hooked up to a 40 amp breaker via 8/3 romex wire. We are replacing this with an all gas range/oven that only requires 120 volts/15 amp breaker. My question is can I use the existing 8/3 wire by splicing 12/2 via one junction box at the service panel end and another box in an accessible spot just before the new oven, capping off the red wire at both ends? I'd then replace the 40 amp breaker with a 15 amp and connect 12/2, then connect the other spliced 12/2 into a new receptacle for the oven.
My original plan was just to attach fishing wire to the existing 8/3, pull out the 8/3 from the service panel, then attach 12/2 to the fishing wire and fish that through to the service panel. I will go this route if I have to but it involves several cuts into drywall, undoing bulkheads and acoustic tiles, etc.
electrical oven
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04
add a comment |
Afternoon,
We currently have a gas range cook top with electric oven underneath that is hooked up to a 40 amp breaker via 8/3 romex wire. We are replacing this with an all gas range/oven that only requires 120 volts/15 amp breaker. My question is can I use the existing 8/3 wire by splicing 12/2 via one junction box at the service panel end and another box in an accessible spot just before the new oven, capping off the red wire at both ends? I'd then replace the 40 amp breaker with a 15 amp and connect 12/2, then connect the other spliced 12/2 into a new receptacle for the oven.
My original plan was just to attach fishing wire to the existing 8/3, pull out the 8/3 from the service panel, then attach 12/2 to the fishing wire and fish that through to the service panel. I will go this route if I have to but it involves several cuts into drywall, undoing bulkheads and acoustic tiles, etc.
electrical oven
Afternoon,
We currently have a gas range cook top with electric oven underneath that is hooked up to a 40 amp breaker via 8/3 romex wire. We are replacing this with an all gas range/oven that only requires 120 volts/15 amp breaker. My question is can I use the existing 8/3 wire by splicing 12/2 via one junction box at the service panel end and another box in an accessible spot just before the new oven, capping off the red wire at both ends? I'd then replace the 40 amp breaker with a 15 amp and connect 12/2, then connect the other spliced 12/2 into a new receptacle for the oven.
My original plan was just to attach fishing wire to the existing 8/3, pull out the 8/3 from the service panel, then attach 12/2 to the fishing wire and fish that through to the service panel. I will go this route if I have to but it involves several cuts into drywall, undoing bulkheads and acoustic tiles, etc.
electrical oven
electrical oven
asked Nov 26 '18 at 18:47
Lucas BarwickLucas Barwick
61
61
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04
add a comment |
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04
add a comment |
1 Answer
1
active
oldest
votes
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
|
show 3 more comments
Your Answer
StackExchange.ready(function() {
var channelOptions = {
tags: "".split(" "),
id: "73"
};
initTagRenderer("".split(" "), "".split(" "), channelOptions);
StackExchange.using("externalEditor", function() {
// Have to fire editor after snippets, if snippets enabled
if (StackExchange.settings.snippets.snippetsEnabled) {
StackExchange.using("snippets", function() {
createEditor();
});
}
else {
createEditor();
}
});
function createEditor() {
StackExchange.prepareEditor({
heartbeatType: 'answer',
autoActivateHeartbeat: false,
convertImagesToLinks: false,
noModals: true,
showLowRepImageUploadWarning: true,
reputationToPostImages: null,
bindNavPrevention: true,
postfix: "",
imageUploader: {
brandingHtml: "Powered by u003ca class="icon-imgur-white" href="https://imgur.com/"u003eu003c/au003e",
contentPolicyHtml: "User contributions licensed under u003ca href="https://creativecommons.org/licenses/by-sa/3.0/"u003ecc by-sa 3.0 with attribution requiredu003c/au003e u003ca href="https://stackoverflow.com/legal/content-policy"u003e(content policy)u003c/au003e",
allowUrls: true
},
noCode: true, onDemand: true,
discardSelector: ".discard-answer"
,immediatelyShowMarkdownHelp:true
});
}
});
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2fdiy.stackexchange.com%2fquestions%2f151330%2fnew-oven-range-wiring%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
1 Answer
1
active
oldest
votes
1 Answer
1
active
oldest
votes
active
oldest
votes
active
oldest
votes
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
|
show 3 more comments
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
|
show 3 more comments
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.
edited Nov 26 '18 at 19:02
manassehkatz
10.9k1440
10.9k1440
answered Nov 26 '18 at 18:59
longnecklongneck
14.5k23359
14.5k23359
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
|
show 3 more comments
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
OK - I was just concerned about having space for a pigtail in the new receptacle box, going from 8 gauge to 12 gauge.
– Lucas Barwick
Nov 26 '18 at 19:04
1
1
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
If it's a tiny single-gang box, you're probably right. But if it was done right with a double-gang box, you should be fine.
– longneck
Nov 26 '18 at 19:05
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
You don't even need a pigtail in the service panel if the new breaker can take #8. Many can.
– Harper
Nov 26 '18 at 19:31
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
I just saw this online: reliableparts.ca/product/Gas-Range-Power-Adapter-1515526/475472 Seems too good to be true. Does this just plug into the 220 receptacle that my current oven is using, and I would plug the new oven into the adapter? Would I still need to change the breaker?
– Lucas Barwick
Nov 26 '18 at 20:09
1
1
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
Why new work? You probably want an old work box. But your plan sounds OK.
– longneck
Nov 26 '18 at 20:31
|
show 3 more comments
Thanks for contributing an answer to Home Improvement Stack Exchange!
- Please be sure to answer the question. Provide details and share your research!
But avoid …
- Asking for help, clarification, or responding to other answers.
- Making statements based on opinion; back them up with references or personal experience.
To learn more, see our tips on writing great answers.
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2fdiy.stackexchange.com%2fquestions%2f151330%2fnew-oven-range-wiring%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
See diy.stackexchange.com/questions/150236/…
– longneck
Nov 26 '18 at 19:04